Residential Panel Location

Status
Not open for further replies.

darrenh

Member
Location
Louisiana
I was wondering if putting a panel in a attic that is decked with plenty of walking space, illumiated very good, and has access by stairs would be any violation of the NEC? Only thing I see that could be questioned is if its readily accessible or not.
 
I was wondering if putting a panel in a attic that is decked with plenty of walking space, illumiated very good, and has access by stairs would be any violation of the NEC? Only thing I see that could be questioned is if its readily accessible or not.
As long as it meets 110.26 I see it as no different than if it were in a garage. We all know how that goes, move car, bicycles, boxes and the lawnmower and you might make it to the panel.
 
Thanks, I didn't see any violation either. I was just wondering if the inspector would frown upon it because the stairs to the attic is in the garage.
 
I have done a few in my days. I have never had an issue with it as long as 110.26 is met. In your case I see the panel as readily accessible.
 
Do it quite often here when finishing out the bonus space over a garage. Then again most of those are in walk in attics, but I see no difference if you have permanent stairs.
 
Can you be more specific in describing the panel. Is it a service panel or a remote panel? Where is the main disconnect (Main Breaker)?

Thanks
I don't see where it would matter if it were a service or feeder supplied panel. You want minimal service conductors entering the structure just like you would on any other floor. It is likely longer distance to grounding electrodes, but there is no limitation on length of grounding electrode conductors.
 