highendtron
Senior Member
A general contractor built a bathroom around an existing 200 amp panel. The inspector/ home owner/realtor picked a wall 6' away. The inspector thought it could be done with a 10' service cable. The utility is coming out Tuesday to pull the meter and the inspection is the same day to get the meter put back in. I was thinking no big deal, have the meter pulled, splice and transfer the branch circuits, hook up the service entrance cable, inspect it, plug the meter in, test it, and go home. I set the new panel but the new service cable 4/0,4/0,2/0 is 15' long ( routed up through the bottom part of the ceiling and down the walls). I probably need to set an outside disconnect (because of the length of the service entrance cable) run 4/0,4/0,2/0 to the meter can, and run 4/0,4/0,2/0,2/0 from the disconnect to the panel. I still have time but wanted to run this by the forum for comment.