I have run into a curious question in regards to the International Residential Code (IRC) electrical section dealing with swimming pools.
The 2009 IRC seems to permit the use of AC cable for interior wiring for the feeder to pool equipment as well as the branch circuit wiring for pool motors, packaged spas and hot tubs and wet niche lights.
Now the 2009 IRC electrical section is supposed to be based on the 2008 NEC.
The question I have is I don't see where the 2008 NEC permits the use of AC cable as a wiring method for residential pools.
680.21(A)(4) permits any Chapter 3 wiring method to be used where there is an insulated copper equipment grounding conductor. It goes on to say that where run in a cable the EGC shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly.
I don't see AC cable as complying with this section.
Any thoughts?
Chris