Should the portable genset get it’s own ground rods or just bond to the existing GEC? Seems to me the point is to trip existing overcurrent and/or GFCI devices for safety.
In most cases neither unless for some reason the portable generator is set up as a SDS. Most residential systems with a small generator, inlet, and interlock are set up as a non-SDS.Should the portable genset get it’s own ground rods or just bond to the existing GEC?
It’s bonded to the EGC which it’s only purpose is to trip OCPD’s and GFCI’sThe GE does not have anything to do with tripping OCPD's.
So just a 3 wire connection?In most cases neither unless for some reason the portable generator is set up as a SDS. Most residential systems with a small generator, inlet, and interlock are set up as a non-SDS.
An SDS would be a 3-wire connection similar to a service. A non-SDS would be a 4-wire connection where the neutral and EGC within the generator are not bonded together. The SDS would require a connection to the building grounding electrode system (GES). The non-SDS would not require a connection to any electrodes or the building GES.So just a 3 wire connection?
Exactly how I was planning on connecting it.
There are a few options. Non-SDS is IMO the best because it's the least amount of work for the same result. Whatever system you decide to install don't forget the required signage in Article 702.Exactly how I was planning on connecting it.