Why is anyone talking about sync? If you have two manual transfer switches, or even ATS's, each genny feeds separate load centers even though the load centers are fed from the same panel. Nothing goes back through the panel; "Never the twain shall meet". Don't make it more complicated than necessary.

It was not made all that clear if we are supplying same load(s) with two generators or if each generator is to supply separate loads.

Syncronization becomes necessary if both are to supply same loads
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
It was not made all that clear if we are supplying same load(s) with two generators or if each generator is to supply separate loads.

Syncronization becomes necessary if both are to supply same loads

Yea, the op has not responded to clarify this, so all we are doing is guessing. (which is what we do best anyway!)
 

mtnelectrical

Senior Member
Sorry guys, I was very busy repairing pulled out services and broken meter pans. Well any way, my situation was exactly like the picture. So, not sync is required. Thanks for all your input.
 