olly
Senior Member
- Location
- Berthoud, Colorado
- Occupation
- Master Electrician
I have a outdoor breaker panel, I have a 1 1/4 male adaptor I will use for a chase for the home runs. (probably about 10 romex wires) I plan on sealing with expanding foam when done. How many wires can I have pass through there? I sure as hell don't want to derate my conductors, but I don't believe I need to since the "raceway" is under 18". The chase itself is only as long as a male adaptor.
Could someone let me know what the rule is with this situation? When you use one big hole to pass all your wires through.
Thanks!
Could someone let me know what the rule is with this situation? When you use one big hole to pass all your wires through.
Thanks!