Residential Range Circuit Calculation

Status
Not open for further replies.

Mustwin351

Senior Member
Location
Texas
I am looking at getting a new range but am a little unclear on the circuit required. It is a Fridigaire model fgef3035rf. http://www.frigidaire.com/Kitchen-Appliances/Ranges/Electric-Range/FGEF3035RF/?bvstate=pg:2/ct:r

According to its specifications it is rated at 13.5Kw. The nec for household ranges appears to only address single ranges below that Kw rating. So do I size my circuit as a continuous load at 125% of the name plate rating? (1.25X13.5Kw/240v=70.31 amps) So a 70 amp breaker? That does not seem right.


Interesting when you look up the specifications of this model fgef3035rf on fridgidaire's website the specifications state a minimum circuit of 40 amps is required. But if you read the installation instructions it does not state the required minimum circuit and has this strange table:

Please help me make sense of this.
 

Attachments

  • IMG_4283.jpg
    IMG_4283.jpg
    117.8 KB · Views: 8

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Note 1 to the table

12kw range-- demand is 8 kw plus 5% for each kw or major fraction over 12kw

13.5 kw- 12kw = 1.5 kw-- rounds to 2 kw

2kw X 5%= 10 %

8kw * 1.1= 8.8 kw

8800/240 = 36.67 amps or #8
 

Mustwin351

Senior Member
Location
Texas
Note 1 to the table

12kw range-- demand is 8 kw plus 5% for each kw or major fraction over 12kw

13.5 kw- 12kw = 1.5 kw-- rounds to 2 kw

2kw X 5%= 10 %

8kw * 1.1= 8.8 kw

8800/240 = 36.67 amps or #8


I thought table 220.55 and Note 1 only applied if you had more than one cooking appliance and none of them could be over 12kw....Since my individual range is 13.5kw I didn't think I could use that method of calculation.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I thought table 220.55 and Note 1 only applied if you had more than one cooking appliance and none of them could be over 12kw....Since my individual range is 13.5kw I didn't think I could use that method of calculation.

The range table is supposed to be simple but it is not..... Trust me I did it correctly Read the second sentence in note 1

For ranges individually rated more than 12 kW but not more than 27 kW, the maximum
demand in Column C shall be increased 5 percent for each additional kilowatt of rating or major fraction thereof by which the rating of individual
ranges exceeds 12 kW.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Many ranges can be on a 40 amp circuit with a 50 amp receptacle. Just a note 40 amps is typically the minimum size required. {210.19(A)(3)}
 

Mustwin351

Senior Member
Location
Texas
Many ranges can be on a 40 amp circuit with a 50 amp receptacle. Just a note 40 amps is typically the minimum size required. {210.19(A)(3)}

Interesting that a 20 amp receptacle is not allowed on a 15 amp circuit but a 50 amp receptacle is allowed on a 40 amp circuit.

I guess the odds of overloading the 15 amp circuit are greater but even still why present an opportunity for someone to overload a 40 amp circuit by allowing a 50 amp receptacle on it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Interesting that a 20 amp receptacle is not allowed on a 15 amp circuit but a 50 amp receptacle is allowed on a 40 amp circuit.

Your statement is correct if you have more than one receptacle on the circuit say a 20 amp duplex on a 15 amp circuit. If you're using a single receptacle you can put a 20 amp receptacle on a 15 amp circuit.

For a range you won't find a 40 amp receptacle so the single 50 amp on the 40 amp circuit is OK.
 