No such requirement that I'm aware of.

210.52(A) would require one 6' from a door measured horizontally along the floor line in any unbroken wall space that is 2ft or more in width.
 
Last edited:
I was just pointing out that the wall space behind the door counts. Probably has nothing to do with your question. :)
 