I need some advice from my peers on how to properly advise the homeowner on a service call. I was called out because the power to her KitchenAid built-in was out. I found a counter top GFI tripped that wouldn't reset. When I unplugged the fridge (after a nightmare of pulling it out) the GFI reset and held. When I plugged it back in it popped. when I tried another GFI circuit, popped again. When I tried a non-GFI outlet it held. Everything appeared to be fine. I took amp readings on hot, neutral, and ground individually at the outlet and the readings were floating between .8 and .6 amp, then would spike and fall, I couldn't tell if there was something wrong with my tester. At first I thought I was getting .02-.04 amps on the ground, but then I was also getting .02 in air, so that may have been the tester.
Appliance repair guy (via phone call) says that it needs to be plugged in to a nonGFI outlet. But it had been this way for 12 years. It's holding now that I pulled to the line side of the GFI.
Do I insist that she have the appliance guy find why it trips a GFI and correct it?
Or do I let the appliance get away with "an older appliance can't be on a GFI"?
If he sticks with that, do I recommend she buy a new one?