New guy. Been lurking and reading for the last few weeks and have managed to thoroughly confuse myself.
I am designing a 320A Pedestal mount for a new residence. The pedestal contains the meter socket, 2-200A service disconnects and a 4-slot load center buss connected to one of the breakers.
The GEC originates at two ground rods 8' apart at the pedestal and is landed on the equipment ground and the MBJ is in place.
Each 200A breaker will feed a 200A MB load center in the basement. I will size the conductors as a 4-wire feeder using T310.16 with #4Cu as EGC.
Questions: Now that the footings are ready to pour I need to tie the CEE to the GEC. I would also like to pick up the steel well casing on the same path.
1) I think the proper way is to run a #4 Bare CU to either one of the ground rods or to the Ground Bus in the service disconnect?
2) Can I stub up from the CEE with a #4 to the MB Load centers in the basement or does this create a parallel path to ground? The purpose of this connections is mainly for intersystem bonding.
I am designing a 320A Pedestal mount for a new residence. The pedestal contains the meter socket, 2-200A service disconnects and a 4-slot load center buss connected to one of the breakers.
The GEC originates at two ground rods 8' apart at the pedestal and is landed on the equipment ground and the MBJ is in place.
Each 200A breaker will feed a 200A MB load center in the basement. I will size the conductors as a 4-wire feeder using T310.16 with #4Cu as EGC.
Questions: Now that the footings are ready to pour I need to tie the CEE to the GEC. I would also like to pick up the steel well casing on the same path.
1) I think the proper way is to run a #4 Bare CU to either one of the ground rods or to the Ground Bus in the service disconnect?
2) Can I stub up from the CEE with a #4 to the MB Load centers in the basement or does this create a parallel path to ground? The purpose of this connections is mainly for intersystem bonding.