prattz99
Member
- Location
- Long Island NY
- Occupation
- Electrician
Hi,
I'm looking to have someone check me out on my calculations for residential service that I've been asked to size.
The square footage of the house's livable space totals 3,234 sq' x3 VA=9,702
The appliances I have calculated are:
2 dishwashers 3,000va
1 refrigerator 1,500va
1 freezer 1,500va
3 counter top circuits 4,500va
1 washing machine 1,500va
1 dryer 5,000va
1 microwave circuit 1,500va
5 bathroom circuits 7,500va
1 gas stove w/ 30 amp receptacle 5,000va
2 ac compressors 7,000va
2 air handlers 3,000va
1 9kw steam generator 9,000va
1 gas furnace 500va
for a total of 60,202va
I then deduct 3,000va
with a remainder of 57,202
57,202 x.35 =20,020va
20,020 + 3,000= 23,020va / 240= 85 amps
Is this right? The dwelling unit can have all of this and only require 100 amps for the service?
Also any Mike Holt products that could help me along this process would be great!
I'm looking to have someone check me out on my calculations for residential service that I've been asked to size.
The square footage of the house's livable space totals 3,234 sq' x3 VA=9,702
The appliances I have calculated are:
2 dishwashers 3,000va
1 refrigerator 1,500va
1 freezer 1,500va
3 counter top circuits 4,500va
1 washing machine 1,500va
1 dryer 5,000va
1 microwave circuit 1,500va
5 bathroom circuits 7,500va
1 gas stove w/ 30 amp receptacle 5,000va
2 ac compressors 7,000va
2 air handlers 3,000va
1 9kw steam generator 9,000va
1 gas furnace 500va
for a total of 60,202va
I then deduct 3,000va
with a remainder of 57,202
57,202 x.35 =20,020va
20,020 + 3,000= 23,020va / 240= 85 amps
Is this right? The dwelling unit can have all of this and only require 100 amps for the service?
Also any Mike Holt products that could help me along this process would be great!