residential service gounding

Status
Not open for further replies.

tower

Member
Location
Massachusetts
when driving a ground rod at the meter location do you also have to bring a grounding conductor from the service panel to both sides of the water main? I now you need to bring it from the meter to the panel.

[ April 07, 2003, 08:01 PM: Message edited by: tower ]
 

bill addiss

Senior Member
Re: residential service gounding

tower,

Do you mean both sides of the Water Meter?
If there is a metal yoke across it you may not have to but you had better check with your local inspectors and POCO to find out for sure.

Bill
 

tower

Member
Location
Massachusetts
Re: residential service gounding

I`m sorry. what I meant was driving a ground rod at the electric meter, if so do you also need to run a ground from the service panel to the water meter ( both sides )?also can you recomend a good reference book on resedential electrical work ?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: residential service gounding

The metallic water line must be grounded if it qualifies as a grounding electrode, IE has ten feet in contact with the soil. Any removable device has to have jumper around it. If the water line is not a grounding electrode, then the connection to the water line is a bonding connection.

You may need two ground rods to supplement your water line.

There is a lot more to grounding an electrical service, you may be able to pick it up from a book. The best is "Wiring Simplified", its about $10.00 often will be at the big box stores. Read it, do your self a favor and call a qualified electrican, even if for just a job site consult. The money you spend will save you time and possibly a violation on your inspection.
 