Re: Residential service grounding
250.30 has nothing to do with SERVICE equipment.
250.24 has to do with services, then go to 250.28, 250.50.
My take is; The Grounded Service Entrance conductor is permitted to be grounded at any point from the Service Point to the Disconnect enclosure.
Since the meter grounded conductor is factory grounded to the metal enclosure and if a metal raceway is used between the meter enclosure and the main disconnect enclosure, there is always a parallel path.
This practice is many code cycles old and there has been proposals to prohibit this parallel path which the CMP has not accepted.
In the last 3 or 4 code cycles, this parallel path has been getting more attention though.
Even though the voltage drop on/of the metal enclosure between the meter and the main disconnect is ususally very low, the amperes actually carried by the metal raceway can be more than the current carried by the grounded conductor with-in the metal raceway when the grounded conductor is carrying considerable un-balanced current.
Example: A 200A dwelling service with the grounded conductor ( 8 feet of 2/0 Cu between the meter and the Main OCPD) carrying 30 amps of unbalanced current that is in 5' of RMC , the 2/0 copper conductor is carrying 11.99A and the 2" RMC is carrying 18.01A.
The voltage drop is 0.0093V for the 5' or so in the RMC.
The above study was with resistive loads only.
The above study shows that the RMC is almost carrying 2 times the 2/0 copper conductor current.
There must be many thousands such services in use today.
Until the electronic age, I do not beleive it caused much of a problem, but now, the non-linear loads!
gwz2