Michael Duffy
Member
- Location
- Redding, California
BACKGROUND INFO:
Utility enters the property from overhead pole transformer. The service the runs underground in 2 inch PVC containing three 4/0 aluminum conductors approximately 315 feet. I calculate 5% voltage drop (not the point of the question because it is existing). Conductors terminated into 200 amp residential meter combination panel. The house is using around 11K KWH/yr.
MORE BACKGROUND INFO:
Customer purchased 19.8 KW solar system to connect to this residential service.
QUESTION:
The breaker that ties the solar into the main panel is a 2 pole 125 amps. This would greatly exceed the 200 amp bus withing that main panel. To comply, the panel requires a 385 amp buss (400). Upgrading the service to 400 amp would incur a huge cost of replacement of the underground from the utility pole to the existing 200 amp meter combination panel. I suggested to install a 400 amp meter combination panel and de-rate the main breaker to 200 amps, leaving the existing underground as it is. Am I creating a violation ANYWHERE? I am asking for permission, not forgiveness.
Utility enters the property from overhead pole transformer. The service the runs underground in 2 inch PVC containing three 4/0 aluminum conductors approximately 315 feet. I calculate 5% voltage drop (not the point of the question because it is existing). Conductors terminated into 200 amp residential meter combination panel. The house is using around 11K KWH/yr.
MORE BACKGROUND INFO:
Customer purchased 19.8 KW solar system to connect to this residential service.
QUESTION:
The breaker that ties the solar into the main panel is a 2 pole 125 amps. This would greatly exceed the 200 amp bus withing that main panel. To comply, the panel requires a 385 amp buss (400). Upgrading the service to 400 amp would incur a huge cost of replacement of the underground from the utility pole to the existing 200 amp meter combination panel. I suggested to install a 400 amp meter combination panel and de-rate the main breaker to 200 amps, leaving the existing underground as it is. Am I creating a violation ANYWHERE? I am asking for permission, not forgiveness.