residential service upgrade - my own house

Status
Not open for further replies.

malachi constant

Senior Member
Location
Minneapolis
First off, my credentials. Not a licensed electrician but am a PE. I worked summers in college for an electrical contractor and have rewired my house (it was installed in 1923 with ELECTRICAL CONDUIT!!! so was able to pull new wire & ground one circuit at a time over the years) so have enough hands on experience to be comfortable. The state I live in has no issue with homeowners doing their own electrical work - I've already checked with the electrical inspector and the permit office, and they were 100% on board with me doing the work.

My existing panel is 240 single phase, has a 50A or 60A main breaker and (I believe, off the top of my head) sixteen branch breakers, probably 50-60 years old. (Which begs the question, did they even make breaker load centers back then?) Planning to upgrade, at least to a 100A, maybe a 200A. I have tripped the main once or twice in ten years, but the real reason for the upgrade is wanting to add a couple circuits to my kitchen - just no space in the panel at all. A subpanel is a plausible but very dumb idea with only a 50A service - might as well do this right.

I was all set to pull the trigger and get the project started when I called the Utility to schedule an outage while I changed it over. No problem on their end. Then I asked, hey, if I'm upgrading the panel shouldn't you be upgrading the overhead? They said, sure, we can do that, since it is an upgrade it will be no cost to you. BUT. The overhead mast and meter socket is customer owned. You (they say to me) will have to replace that yourself.

So here's the thing. I am not going to replace the mast myself. If it needs replaced I'll hire an electrician, I know enough of them. But DOES the mast need replaced? I am not really increasing load - maybe the microwave and toaster will run concurrently, but that's it. No plans for future loads, just adding in the extra capacity because it would be dumb not to. I don't know enough about single-family residential services to know the codes surrounding them. My guess is, yes, the transformer secondaries (overheads, mast, meter socket, etc) are required by code to be upgraded. And even if they are not, do I really want to hook up a couple unprotected #6s on the line side of my panel and risk a fire at that point, inside my house. It would be one thing if all the unprotected undersized wire was hanging in the air - in that case, take the chance, let's see if it burns! But when it is inside your house, that kind of answers the question for me.

One other thing that came to mind as I was writing this out, is maybe the incoming feeders are already #3s or larger - maybe I've got a 50A service with 100A wire feeding it. In that case I could upgrade the panel to 100A and not need to replace the mast. I'll have to check that tonight. If the size markings are not readily visible does anyone have suggestions as to how to visually verify wire gauge?

Regarding replacing the mast, I guess I know the answer. Unless the existing service feeder is big enough I need to get it replaced. I just needed to type it all out to make sense of it, thanks for bearing with me. If anyone has any thoughts/suggestions they are appreciated!

EDIT: Regarding the incoming feeder, I have a photo of it in this previous post: http://forums.mikeholt.com/showthread.php?t=143442
Not sure if you can tell from that photo what size wire that is - not a lot of detail there.
 
Last edited:
I would install new meter can, riser w/XHHW, SE cable the whole shebang for piece of mind. Here if the service drop is supported

by the riser 2" minimun is required. If the drop is attached to a ceramic insulator a 2 X 6 or suitable framing is required.

Then there is underground but POCO wants $750 to change over from OH to UG. Trenching is on homeowner along with conduit.
 
I don't want to be a pain, but just reading your first paragraph, I don't think this thread meets the forum rules.:angel:
 
I don't want to be a pain, but just reading your first paragraph, I don't think this thread meets the forum rules.:angel:

I was thinking that too ... but as I read on, I don't know ... it begins to blur. Apparently, he says that he's going to hire an EC. :?

Anywho, 'round here one needs to certainly pull a permit and the customer is responsible for installing the mast, its leads, the meter box (though utility will furnish), leads/conduit/cable to main panel, grounding and making connections at the meter box. The utility installs a meter and connects wires to mast leads. The leads would need to be sized appropriately based on the NEC. The utility is not governed by the NEC and they need not follow the NEC for their drop from the pole.

When my service was upgraded a few years ago from 100A to 200A they used the same drop and I suspect its the same drop that was there when it went from 60A to 100A many years prior--itty-bitty wires.
 
Planning to upgrade, at least to a 100A, maybe a 200A. I have tripped the main once or twice in ten years, but the real reason for the upgrade is wanting to add a couple circuits to my kitchen - just no space in the panel at all.

If anyone has any thoughts/suggestions they are appreciated!

I would get the advice of an electrician in your area.

Around here I normaly suggest going with a 200 amp up-grade as this is the best all around solution. Many people are going with heat pump and electric back up heat strips and even switching to electric ranges and water heaters. On the other hand if this is a small house with no future plan for a hot tub or to make any changes and you don't plan to sell the house then a 100 amp service may be plenty. If you have any doubts do a load calculation and add any furture up-graded items such as an electric range or water heater.

The reason I say to consult a local electrician is that they will know what is best or required in your area.
 