I have recently seen an electrical installation where a new single family home has a 400a 120/240v 1 ph service. The electrican installed a 400a meter base, then parallel conductors from the meter to two (2) 200a MCB panelboards. From each 200a MCB panel, there was a GEC to an exterior driven gound rod. Also there was no bond between each 200a panelboard.
Any idea where in the NEC this installation is discussed? Is this install acceptable?
My understanding was only one GEC and GES are allowed except in a separately derived system.
I believe the electrician also installed a driven ground rod at the exterior water well. BTW all was inspected and approved by the local electrical inspector.
Thanks for any feedback.