If one were to install a 200 amp disconnect outside next to the meter and then about 30 feet of SER to the panel inside does the disconnect need to be fused? I think the answer is yes but I just want to make sure. Thanks.
M.D. said:230.91 The overcurrent protection shall be an integral part of the disconnect or be located adjacent thereto....
Cable inside or outside ,.. makes no difference ,.. unless you get rid of the disconnect.