Residential Single Phase Range total kW help

Status
Not open for further replies.

Loffgren

Senior Member
Location
CA
ok sorry dumb question, doing a residential load calc. The range in question name plate says 8.6kW and 11.6kw. my assumption is that those are for the top/bottom portions. Would the range be a "20.2kw" range?
Thanks again
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have never seen a range with two kw's given unless that is a 208V and 240V listed range. But even that doesn't add up.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have never seen a range with two kw's given unless that is a 208V and 240V listed range. But even that doesn't add up.

Actually it does add up. 240 v for the 11.6 kw and 208v for the 8.6kw

240* 240/11600= 5 ohms

sq. rt of 8600*5 = 208v
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Sounds right. Resistive power at 208v is approximately 75% of that at 240v.

8.6 / 11.6 = 0.74
 