Re: Residential smoke detectors
In NY State:
Residential Building Code
"R317.1 Single-and multiple-station smoke alarms. Single-and multiple-station smoke alarms shall be located in the following locations.
1. In each sleeping room.
2. Outside of each separate sleeping area in the immediate vicinity of the bedrooms.
3. On each additional story of the dwelling, including basements and cellars but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than on full story below the upper level.
When more than one smoke alarm is required to be installed within an individual dwelling unit the alarm devices shall be interconnected in such a manner that the actuation of one alarm will activate all of the alarms in the individual unit. The alarm shall be clearly audible in all bedrooms over backround noise levels with all intervening doors closed.
All smoke alarms shall be listed and installed in accordance with the provisions of this code and the household fire warning equipment provisions of NFPA 72.
For locations in NFPA 72 : (for more specific requirements)
11.5.1 One-and Two-Family Dwelling Units.
Notice the lack of a requirement to install smoke alarms in BOILER ROOMS, and they are NOT required in unfinished attics.
And of course follow the specific installation instructions from the manufacturer - read the instructions that come with the smoke alarm, as they have a lot of very good information - and are easy to read