residential spa

Status
Not open for further replies.

shelco

Senior Member
Installing a packaged spa for single family home.
8/3 romex to 50a GFI on deck near spa then liquid tite to the spa. I don't do this type of installation very often(or ever). Any Issues?
 
Re: residential spa

Read manufactures instructions, almost every packaged spa requires the equipment grounding conductor to be the same size as the phase conductors, and because of 110.3 (B) you must fulfill that requirement. If spa is a 40 or 50 amp unit, then you cannot run romex to it at all.
Fred Bender
 
Re: residential spa

Thanks
I did mean #6 not #8.
Where in the code does it disallow romex at this amperage. The only reason I planed on this is that almost every spa in this area that I have seen is done this way.
 
Re: residential spa

We have wired 1000`s of spa prewires in 6/3 nm .Never has there been an issue in re: to the grounding conductors size.I don`t see any issue at all ;)
 
Re: residential spa

I didn't see anything wrong either. Where do you normally place the GFCI? In the panel or near the spa?
Thanks
 
Re: residential spa

If the 50A GFCI is in a wet location (outdoors) then Romex cannot be used. Also if the SPA includes a motor, then I believe 680-25(c) requires use of RMC, IMC, RNMC or MC for the outdoor part of the wiring at a one-family dwelling. I am sure we will debate the "Pool associated motors" language.

Mark
 
Re: residential spa

The fact that you have done it once or a thousand times a certain way doesn't make it right. If the manufacturers instructions state a minimum size euipment grounding conductor, then that must be installed. 110.3 (B) is the most widely violated code section! A 6-3 romex in most cases in not legal to run to a packaged spa.

Fred Bender
 
Re: residential spa

Sorry but if you can show me an actual violation I will concede.All that article says it must conform with manufacturers instructions that is the biggest crock that is used as a catch all.
We are contracted to install a 50 amp prewire.As far as nm not being acceptable why not ? It is inside the residence and terminates on the back of a wp disconnect.Any exterior wiring is done in wet location means.Twist the NEC any way you like but unless you can show me an article that explicetly forbids it status quoe for me ;)
 
Re: residential spa

Originally posted by busman:
If the 50A GFCI is in a wet location (outdoors) then Romex cannot be used. Also if the SPA includes a motor, then I believe 680-25(c) requires use of RMC, IMC, RNMC or MC for the outdoor part of the wiring at a one-family dwelling. I am sure we will debate the "Pool associated motors" language.

Mark
You must be using the 05 code we are under the 02 code and 680 25 in 02 doesn`t have a c subsection
 
Re: residential spa

Originally posted by derf48:
A 6-3 romex in most cases in not legal to run to a packaged spa.

Fred Bender
I too would like to see something that proves this.
 
Re: residential spa

Actually using the 1999 code. I have the 02, but my jurisdiction is still on 99.

It could be debated whether the inside of a WP disconnect outdoors fed from the back is a wet or dry location.

Mark

[ May 18, 2005, 06:23 PM: Message edited by: busman ]
 
Re: residential spa

I agree that from the disc to the spa needs to be in cond. or liquidtite flex but to the disc I don't see where nm is a violation. The code specificaly staes that wiring inside of the residence to an outside spa can be NM.
 
Re: residential spa

I don't think it is something in explicit writing.
I do understand what derf is saying. If the instructions say torun a #6 ground for the WHOLE circuit, then you must do so. I have not seen this in any instructions.
In fact, if the circuit hits a w/p disconnect switch with a breaker, I would call the load side of this the branch circuit. This already needs an insulated ground and is typically the same size as the circuit conductors.


"It could be debated whether the inside of a WP disconnect outdoors fed from the back is a wet or dry location."
I agree. IMO this is NOT a wet or damp location. The same argument could be made for all those areas with outside main panels. If this argument were held up, then any place with a panel outside would need UF as the originating branch circuit conductors. I don't think that's going to happen.
 
Re: residential spa

I've done hundreds of spas also.
Every single one has required a full size, insulated ground.
NM would be no good.

Allen, if all you are asked to provide is a 50 amp circut, you are correct.
But if the circut is to be used for a spa, your wire, at that point is probably violating the manufacturers instructions.
If you know ahead of time that the circut is for a spa, it is possible that you are doin the customer a dis-service, imo.
 
Re: residential spa

Peter,

I tend to agree with you, I was just pointing out that an AHJ could probably see it either way. If given the choice in this condition (i.e. new circuit), I would probably run UF to avoid the question.

Also, the original post did not say that the disconnect was fed from the back. I was partially commenting on the fact that there might have been a run of NM outdoors.

Mark

[ May 18, 2005, 07:36 PM: Message edited by: busman ]
 
Re: residential spa

I would like to know how an over sized grounding conductor will ever make a GFCI (class A I might add)protected spa installation any safer???
This requirment is so riddled with holes that it makes my head spin!

1. A properly connected # 10 grounding conductor will fault the whole 60 amps the circuit can give it!
2. It most likly will not ever see this high of current as it has a GFCI breaker ahead of it which should only let it see 5ma's

3. A over sized ground will not fix a badly connected grounding conductor, a bad connection is a bad connection.
It happen's on big and little wires

One question I have is are these the "UL listed" instruction's? If not then 110.3 does not apply, and I can't see UL making a requirment like this. :roll:
 
Re: residential spa

Originally posted by busman:
Actually using the 1999 code. I have the 02, but my jurisdiction is still on 99.

It could be debated whether the inside of a WP disconnect outdoors fed from the back is a wet or dry location.

Mark
the 1999 cycle states in

680-40. Outdoor Installations
A spa or hot tub installed outdoors shall comply with the provisions of Parts A and B of this article except as permitted in (a) and (b).


680-25 (c) Motors. Pool-associated motors shall be connected to an equipment grounding conductor sized in accordance with Table 250-122 but not smaller than No. 12. It shall be an insulated copper conductor and shall be installed with the circuit conductors in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the application. Where installed on or within buildings, electrical metallic tubing shall be permitted to be used to protect the conductors.
In the interior of a one-family dwelling or in the interior of another building or structure associated with a one-family dwelling, any of the wiring methods recognized in Chapter 3 of this Code that contain a copper equipment grounding conductor that is insulated or covered by the outer sheath of the wiring method and is not smaller than No. 12 shall be permitted to be used for the connection of pool-associated motors. Flexible cord shall be permitted in accordance with Section 680-7.

Does this spa have a motor?

edited to add the dwelling unit part

:)

[ May 18, 2005, 08:19 PM: Message edited by: jwelectric ]
 
Re: residential spa

Originally posted by jwelectric:
Originally posted by busman:
Actually using the 1999 code. I have the 02, but my jurisdiction is still on 99.

It could be debated whether the inside of a WP disconnect outdoors fed from the back is a wet or dry location.

Mark
the 1999 cycle states in

680-40. Outdoor Installations
A spa or hot tub installed outdoors shall comply with the provisions of Parts A and B of this article except as permitted in (a) and (b).


680-25 (c) Motors. Pool-associated motors shall be connected to an equipment grounding conductor sized in accordance with Table 250-122 but not smaller than No. 12. It shall be an insulated copper conductor and shall be installed with the circuit conductors in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the application. Where installed on or within buildings, electrical metallic tubing shall be permitted to be used to protect the conductors.

Does this spa have a motor?

:)
I`ll jump and say that the keyword is outdoor installation.From disconnect to unit.Once you reach the gfci disc. that is a new sub panel.Anything after that would have to comply.Again enter the back in 6/3 nm and it is fine.Still a dry location in house and as far as being code compliant to feed a sub panel it is fine :p Nothing says it has to compy from main panel to sub panel that is already taken care of but if manufacturers instructions did say this then it would only be from point of usage and not point of origin.
Even if you subed a 200 amp panel and took power from there that would not comply with the supposed manufacturers instructions.Look at200 amp al ser that would not be ok,so to say that .The point of origin could only be from a MBR panel and not a sub panel :eek:
 