8/3 romex is only good for 40 amps. See table 310.16 and 334.80Originally posted by shelco:
8/3 romex to 50a GFI on deck near spa then liquid tite to the spa. Any Issues?
You must be using the 05 code we are under the 02 code and 680 25 in 02 doesn`t have a c subsectionOriginally posted by busman:
If the 50A GFCI is in a wet location (outdoors) then Romex cannot be used. Also if the SPA includes a motor, then I believe 680-25(c) requires use of RMC, IMC, RNMC or MC for the outdoor part of the wiring at a one-family dwelling. I am sure we will debate the "Pool associated motors" language.
Mark
I too would like to see something that proves this.Originally posted by derf48:
A 6-3 romex in most cases in not legal to run to a packaged spa.
Fred Bender
the 1999 cycle states inOriginally posted by busman:
Actually using the 1999 code. I have the 02, but my jurisdiction is still on 99.
It could be debated whether the inside of a WP disconnect outdoors fed from the back is a wet or dry location.
Mark
I`ll jump and say that the keyword is outdoor installation.From disconnect to unit.Once you reach the gfci disc. that is a new sub panel.Anything after that would have to comply.Again enter the back in 6/3 nm and it is fine.Still a dry location in house and as far as being code compliant to feed a sub panel it is fineOriginally posted by jwelectric:
Mark
680-40. Outdoor Installations
A spa or hot tub installed outdoors shall comply with the provisions of Parts A and B of this article except as permitted in (a) and (b).
680-25 (c) Motors. Pool-associated motors shall be connected to an equipment grounding conductor sized in accordance with Table 250-122 but not smaller than No. 12. It shall be an insulated copper conductor and shall be installed with the circuit conductors in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the application. Where installed on or within buildings, electrical metallic tubing shall be permitted to be used to protect the conductors.
Does this spa have a motor?