Mkopro97
Member
- Location
- Boulder Colorado
When installing a 16KW 120/240v standby generator I was wondering if I need to bond the EGC to the neutral bus in the transfer switch? It is bonded at the main panel. I am thinking that this generator would not be a be a separately derived system so I would not bond in the transfer switch. Appreciate you thoughts. Thanks.