N nizak Senior Member Mar 17, 2025 #1 Would a steam generator and a hot tub have to be figured at 100% for a load calculation ? Thank you
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Mar 17, 2025 #2 Will they run at full load continuously for three hours or more? That would be the determining factor.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Mar 17, 2025 #3 Are you asking about 100% or 125% or something else?
N nizak Senior Member Mar 18, 2025 #4 infinity said: Are you asking about 100% or 125% or something else? Click to expand... In the load calculation can it be included along with the electric clothes dryer and range or would it be figured at the full nameplate like the AC?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 18, 2025 #5 Imo, they are figured at 100% for the standard calc but they would get the relief in the option as it will be part of the percentage taken