Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
I have to add two single 20 amp AFCI circuits to a single family home that has a 100 amp Square D QO panel (Picture attached). This is the first time I will be doing work at this residence. It appears that someone has fed the range with a 60 Amp DP breaker, and the Dryer with a 50 Amp DP breaker, these are the largest loads.
I was thinking of adding a 6 or 8 circuit MLO panel and feeding it with a 60 amp breaker. I would feed the MLO panel with #6 THHN and a #8 ground. As you can see the neutral bar is a bit jammed, so I'm concerned about fitting the neutral and ground of a subpanel on there. Do they make a lug that you could add this type of Square D neutral bar? Is the subpanel the way to go, or do you have any other ideas? The homeowner has no intentions of adding onto the house, or having the service upgraded. Thank you for your help
![1626541573891.png 1626541573891.png](https://forums.mikeholt.com/data/attachments/20/20896-c62f709369f9730b111e4fb34056c6f8.jpg)
I was thinking of adding a 6 or 8 circuit MLO panel and feeding it with a 60 amp breaker. I would feed the MLO panel with #6 THHN and a #8 ground. As you can see the neutral bar is a bit jammed, so I'm concerned about fitting the neutral and ground of a subpanel on there. Do they make a lug that you could add this type of Square D neutral bar? Is the subpanel the way to go, or do you have any other ideas? The homeowner has no intentions of adding onto the house, or having the service upgraded. Thank you for your help