Residential tamper-resistant receptacles

Status
Not open for further replies.

JDBrown

Senior Member
Location
California
Occupation
Electrical Engineer
Pretty much all I do is commercial, so I'm not really up on all the residential requirements, and I want to make sure I've got this straight. NEC 406.11 says:
406.11 Tamper-Resistant Receptacles in Dwelling Units
In all areas specified in 210.52, all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
I went to 210.52, and it seemed to list all 125-volt, 15- and 20-amp receptacles in a residential building. So, are ALL 125-volt, 15- and 20-amp receptacles required to be tamper-resistant when dealing with residential, or are there exceptions that I'm missing?
 
Pretty much all I do is commercial, so I'm not really up on all the residential requirements, and I want to make sure I've got this straight. NEC 406.11 says:

I went to 210.52, and it seemed to list all 125-volt, 15- and 20-amp receptacles in a residential building. So, are ALL 125-volt, 15- and 20-amp receptacles required to be tamper-resistant when dealing with residential, or are there exceptions that I'm missing?

406.12 Tamper-Resistant Receptacles for Dwelling Units. In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Exception:  Receptacles in the following locations shall not be required to be tamper-resistant:
(1) 
Receptacles located more than 1.7 m (5? ft) above the floor.
(2) 
Receptacles that are part of a luminaire or appliance.
(3) 
A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).
(4) 
Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).
 
It is pretty much easier to just use all TRs than trying to stock two kinds and make them end up in the right spots.

Don't forget weather resistant ones for wet locations.
 
Pretty much all I do is commercial, so I'm not really up on all the residential requirements, and I want to make sure I've got this straight. NEC 406.11 says:

I went to 210.52, and it seemed to list all 125-volt, 15- and 20-amp receptacles in a residential building. So, are ALL 125-volt, 15- and 20-amp receptacles required to be tamper-resistant when dealing with residential, or are there exceptions that I'm missing?

406.12 Tamper-Resistant Receptacles for Dwelling Units. In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.

Exception: Receptacles in the following locations shall not be required to be tamper-resistant:

Changed From 2008

?
spacer.gif
406.12 & Exception: Revised to specify that the requirement applies to ?nonlocking? type receptacles and to add a new exception providing specific conditions under which receptacles are not required to be tamper-resistant


(1)
spacer.gif
Receptacles located more than 1.7 m (5? ft) above the floor.

(2)
spacer.gif
Receptacles that are part of a luminaire or appliance.

(3)
spacer.gif
A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).

(4)
spacer.gif
Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).
 
That explains why I didn't see the Exception -- I'm still on the 2008 code (until January 1st). Thanks for the replies.
 