Residential TVSS ?

Status
Not open for further replies.

gb261

New member
I am will be installing a TVSS at the service, which is a 100 amp panel with main breaker. All circuits are being used. The panel manufacture makes a 2 pole TVSS breaker that can replace existing breakers and will allow the branch circuit's to be connect to it.If surge protection is lost, the breaker trips, letting the homeowner know that there is a problem. It can be reset and work like a simple breaker untill it can be replaced. It does appear's that it only does line to line and line to nuetral, whis is fine. There will be point of use TVSS'S, also.
It meets UL 1449 2nd edtion and ANSI C62.11, NOT .41. Will this be alright to use?

Amperage 20 Amp
Number of Poles (2) 1-Pole Circuit Breakers
Initial Clamping Level 240 Volts
Transient Energy Rating 360 Joules line-to-neutral
720 Joules line-to-line

Transient Suppression
Voltage Rating 500 volts peak, line-to-neutral
1000 volts peak, line-to-line

Peak Current Rating (impulse) 40,000 amperes
Discharge Voltage Characteristic @ 1,500A, 600 volts
@ 5,000A, 800 volts
(both line-to-neutral)

Discharge Current Withstand Rating 10,000 amperes
line-to-neutral

Circuit Breaker Interrupting Rating 10,000A, 120/240V AC
House Wiring System Warranty Amount $20,000
Warranty Period 24 months
Lightning Protection No
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Residential TVSS ?

Should be OK, ignore the joules rating, means nothing. No need to worry about L-G and N-G modes, it is already covered by the MBJ.
 