Pump installer called me with some questions with the VFDs they are using on residential homes. Single phase in three out and some can also operate 2 wire pumps. I haven't seen details yet.
Issue at the moment is when the pumps kick on the LEDs blink or flicker. FWIU Franklin makes a filter in the $700 range.
We briefly discussed LED sensitivity to VD. Adding ferrite rings and the super cheap split ones offered on Amazon.
When grounding was brought up, I mentioned adding rods would do nothing. Apparently, not so in his experience. The devil will be in the details but apparently he drilled a hole in the basement floor, added a rod, and bonded directly to the drive. Flicker stopped. IDK if an EG to the line side of the VFD is there or not. I have been invited to look at a couple of homes with the issue including the with the one with the added rod. Worse yet is some homes are not bothered at all.
Any thought as to why a driven rod would help the situation?
EC - retired
It is Franklin 2 wire in/out drives giving the problems. Pump installer thinks one in five gives flicker issue. They set me up with a drive and pump motor to play with today. Optional two wire control starts motor at 35 HZ and ramps up in 3-4 seconds. VD is .5 with Motor load only. No Pump. IIRC it’s been determined here that .5 is enough to cause the dimming/flicker on some dimmable LEDs. It didn’t bother my shop non dimmable. Visit to a job site later this week.
EC - retired
Just what, not why.
Back yesterday and met with pump installer & Franklin Field rep who brought an older Franklin filter with him. The lights had started to blink again while connected to the branch circuit EG a week or so ago. I rigged up a 3 way switch so we could easily alternate from EG to isolated ground rod for easy comparison. Definite difference. Filter worked. A new version was going to be ordered and installed. In this house only the kitchen LEDs were affected.
Went to next house where I was going to watch while their EC did the checks. He couldn't make it, so I brought the meters out again.
Simpler. All the lighting was affected. About a 3 volt drop at start of the pump. SE conductors were typical Al conductors for 200 amp service. I suspect the POCO transformer is @ minimum. Filter made no difference when Field rep installed it.
The filter was interesting in how it could work for different systems and different voltages. The input filter had about a 10% voltage drop.
EC - retired
So the ground rod did eliminate the flickering? Or just reduced it?
Appeared to eliminate it. I didn't include the third option which would have been no connection to either. :oops: I should have.
I am not advocating the removal of a properly installed EG. It was the solution the pump installer came up with and partially why I was called. He knows better. The EG was connected when I left and they were going to suffer with flickering lights until the new part came in.
Tommy1776
SC
Industrial Electrical Maintenance, AAS, CW
Residential well pump using a Franklin water pump VFDs =random LEDs to flicker, what is the name plate data for VFD & pump?
Tommy
EC - retired
I used the three way before the filter was installed. Power in. I also inserted my meter inline to measure amperage. Milliamps. Rod had about 84, EG about 240. IDR exact values but would expect more with the EG. Motor and conductors to it megged 200+M at 500+volts.
Filter had the EG connected as it should.
Jraef
Moderator, OTD
Electrical Engineer
How is the grounding done WRT the motor and VFD? It's always important to run the motor EGC directly to the VFD ground terminal, then run a SEPARATE EGC from the VFD case to the building ground. It you don't the common mode noise from the motor side of the VFD that is trying to get back to it's source (the transistors) will infect your entire ground system. You wouldn't think it would make a difference, but it absolutely does. So maybe the subtle difference in that one out of six installations is that in the other 5, the installer followed the instructions as to where to terminate the motor ground lead, but the 6th installer didn't. That's something that's easy to miss.
I had a VFD service tech point that out to me on a big install at a UPS sortation facility with about 200 VFDs on the conveyors. In one panel with about 40 drives, installed by a different contractor, they had all sorts of screwball issues, but in the other panels that I had worked on, no issues. The new contractor was out there for days, couldn't figure out what was wrong, so they called me because my panels were fine. I too looked at it for half a day and didn't see it. A-B service tech got there after lunch, he saw it right away and when we fixed it by moving the motor ground leads off of the ground bus to the individual ground terminals on the VFDs, all the screwball stuff was gone. The VFD tech explained it to me and sure enough, this was right there in the installation manual for the drives, so my guys had read it and followed it.