I’m installing a 200 amp service on a new dwelling.
Conductors from meter base to service rated transfer switch are 3/0 CU.
Conductors from transfer switch to 200 amp feed through outdoor load center that will be supplying an 100 amp load center in the attached garage are 3/0 CU.
( I have 3/0 CU left over from a prior job, I realize 2/0 CU is compliant for this portion of wiring)
From the feed through load center I have just under 150’ to feed the 200 amp load center located in the basement of the dwelling.
My question is: Would I need 250 AL or could I use 4/0 AL for that?
I feel 250 is the correct answer.
I’m not saying 250 for VD reasons I’m saying it because it’s not supplying 100% of the dwelling.
Another contractor I know is adamant that 4/0 is compliant.
Am I incorrect?
Thanks
Conductors from meter base to service rated transfer switch are 3/0 CU.
Conductors from transfer switch to 200 amp feed through outdoor load center that will be supplying an 100 amp load center in the attached garage are 3/0 CU.
( I have 3/0 CU left over from a prior job, I realize 2/0 CU is compliant for this portion of wiring)
From the feed through load center I have just under 150’ to feed the 200 amp load center located in the basement of the dwelling.
My question is: Would I need 250 AL or could I use 4/0 AL for that?
I feel 250 is the correct answer.
I’m not saying 250 for VD reasons I’m saying it because it’s not supplying 100% of the dwelling.
Another contractor I know is adamant that 4/0 is compliant.
Am I incorrect?
Thanks