We have a 3p 3w solidly grounded 480V system where this is a need to connect a relatively large single phase load. The proposed solution is a 480V - 120/240V single phase transformer to serve a 100kVA (208A at 480V) transformer. My concern is that this 1500 kVA system only has about 75A of 3p load normally and the 3w ground fault protection on the proposed feeder is set to 100A. 75A 0 Deg + 275A 120 Deg + 275A -120 Deg = 200A 180 Deg.
I found this Schneider Electric FAQ that says the trip unit is "not looking for an imbalance" but instead a non-zero vector sum. What am missing here? How could an imbalance result in a zero vector sum? Unless the current phase angles change drastically to compensate, I'm not sure how this is possible.
https://www.schneider-electric.us/en/faqs/FA167448/
Assuming we proceed with this installation (not likely), could this L-L single phase load cause a misoperation of a 3w residual ground fault relay? I know there are better ways to do this but I'm more interested in learning about how residual ground fault would work in this situation than I am in suggestions for how to serve these loads.
I found this Schneider Electric FAQ that says the trip unit is "not looking for an imbalance" but instead a non-zero vector sum. What am missing here? How could an imbalance result in a zero vector sum? Unless the current phase angles change drastically to compensate, I'm not sure how this is possible.
https://www.schneider-electric.us/en/faqs/FA167448/
Assuming we proceed with this installation (not likely), could this L-L single phase load cause a misoperation of a 3w residual ground fault relay? I know there are better ways to do this but I'm more interested in learning about how residual ground fault would work in this situation than I am in suggestions for how to serve these loads.