We have been directed to adjust resistance values downward for voltage drop calculations on a municipal project to comply with NEC. I had already corrected ampacity values to account for more than 3 conductors in shared conduit. I have not found correction factors in NEC to adjust wire resistance. Where can I find this, assuming it is actually in the NEC?
There is no NEC requirement to calculate voltage drop according to a specific method, except in a very limited scope of applications.
For generic applications, the NEC only contains an informational note with recommendations. And there is no procedure for adjusting resistance values for conditions of use.
The resistance values in the NEC are based on 75C conductor temperature, which is well-representative of most of the worst-case conditions which any properly sized wire for ampacity and conditions of use will experience. For several reasons:
1. Most terminations need to be sized per the 75C column of the NEC, before even thinking about conductor type and conditions of use.
2. Temperature is not uniform inside a conductor. Even if the core of the metal achieves 90C, this temperature will decrease farther from the center. The true resistance of the conductor would need to consider the spatial variation of both temperature and the distribution of electrical current.
3. To achieve the high temperatures, it takes a time for a continuous current to accumulate resistive heating to the steady-state temperature. Continuous loads require a 1.25 safety factor on the wire ampacity. So a continuous load will not achieve the full 90C conductor temperature, even if the 90C column of the NEC is relied upon for ampacity calculations.
If you do need to document a calculation, you can apply a temperature correction to the resistance values from 75C to 90C, based on the column of the NEC you rely upon for your ampacity calculations. For instance, consider #8 Cu wire derated at 80% for bundling with a continuous load of 35A. You are relying upon the 55A value in the 90C column. Therefore you can derate copper's resistance of #8 wire from the given value at 75C to the worst-case scenario value at 90C. There is no documentation of this method, and it is very likely overkill to compensate for voltage drop due to this factor.
Anixter has tables which have resistance at 60C, 75C, and 90C:
https://www.anixter.com/content/dam/Anixter/Guide/7H0011X0_W&C_Tech_Handbook_Sec_07.pdf
When I have to upsize wires in extreme excess of their minimum local size due to distance and voltage drop curtailment, I commonly apply the 60C column resistances from the above document. Because the selected wire will likely be sized well within ampacities per the 60C column of the NEC.