ron
- New York, 40.7514,-73.9925
Is anyone aware of a graphic that would help explain the limited ground fault current of a resistance grounded system, during a fault, and how it would effect an electrician while working on the faulted equipment if touched?
I was trying to draw myself a four line diagram to indicate fault current through a worker that may be different then a solidly grounded system. Clearly during a fault on a resistance grounded system, the system is still energized and hopefully in an alarm condition, requiring electricians to make the diagnosis while the equipment is "hot".
Would you consider a resistance grounded system more dangerous to a worker than a solidly grounded system?
I've seen lots of solidly grounded system that have high impedance arc faults, that didn't trip the upstream circuit breakers too.
The graphic will be used for educational purposes within my office.
We design systems that are critical in nature, and can sort of be considered similar to a batch industrial process.