Hello,
I have a 4160V resistance grounded system and have to purchase a MEI switchgear (switches only, no breakers). I am planning on providing metering for this switchgear. The questions that i have are:
Can PT's in this switchgear be WYE connected with a solidly grounded neutral? Or do i have to use open delta connection?
I have a concern that WYE connected PT's might cause the fault current to bypass the resistor and that inbalance in the PT loads might cause current flow back through the resistor creating unnecessary alarm.
Thanks,
Mike