Please explain the resistance using a megger on testing Raychem heat trace , 5 watt , 277 volt
20 amp .
20 amp .
They specify insulation resistance testing prior to startup.Please explain the resistance using a megger on testing Raychem heat trace , 5 watt , 277 volt
20 amp .
Insulation resistance testing (using a megohmmeter) should be conducted at three voltages; 500, 1000, and 2500 Vdc. Significant problems may not be detected if testing is done only at 500 and 1000 volts.
A clean, dry, properly installed circuit should measure thousands of megohms, regardless of the heating cable length or measuring voltage (0–2500 dc). The following criteria are provided to assist in determining the acceptability of an installation where optimum conditions may not apply.
All insulation resistance values should be greater than 1000 megohms. If the reading is lower, consult Section 10, Troubleshooting Guide.
Have never seen that happen with the type of heat trace that has a full braided metal shield under the jacket and over the actual heating tape and I have installed tens thousands of feet of it on industrial projects. I have seen that on some very old heat trace prior to the use of the metal shield and on some of the home use stuff, especially the non-self-regulating types.They are just looking for installation damage, if you don’t do it, and when (not if) it catches fire, your on the hook, not them.
I don't think it does.May I ask what this has to do with PV or anything related?
Probably melting the snow and ice off the panels (burning 2 to 10 times the output of the panel) LOL!May I ask what this has to do with PV or anything related?