I like this thread because I’m having trouble understanding the calculations on a question from a psi practice exam. Is there anyone that can help me out?
Multiple nonmotor generator arc welders are being served by a branch panel. There are two 120-amperes welders with a 70% duty cycle, one 90-amperes welder with a 80% duty cycle, and one 250-amperes welder with a 50% duty cycle. What is the minimum disconnect for this branch panel?
i keep getting 459 but the answer it shows is 450. Am I just to round or did I do something wrong?
NEC 2017I get 458A, so apparently they are rounding off their answer.
Hey i replied to theThe amount of conductor heating at any given time is proportional to the current squared ( i.e, I²R ).
The effective current that topgone mentioned is the amount of continuous current (i.e., at a 100% duty-cycle) that would produce the same amount of heating as the actual current that has a duty cycle D%.
D% = 50% means the welder is on for 1/2 of the time during the standard 10 minute period.
Therefore to get an equivalent amount of heating:
(effective current)² x 100% = (actual current)² x duty-cycle D%
After dividing by 100% and taking the square root on both sides of the equation:
effective current = actual current x √( duty-cycle D% / 100%)
And so the multiplier to use for calculating effective current is: √( duty-cycle D% / 100%)
And so as topgone mentioned you get the numbers in the table such as:
√( 40% / 100%) = 0.63
√( 25% / 100%) = 0.5
...etc.
ok but if that’s minimumI get 458A, so apparently they are rounding off their answer.
OH I see what you did. I didn’t account the second 100% to the equation . Thank you!NEC 2017
630.11(B) Grouping of Welders ....currents determined in 630.11(A) as sum of 100 percent of the two largest welders, plus 85 percent of the third largest welder, plus 70 percent of the fourth largest welder ......
You were calculating at 100% for all loads
Thus my calculations I have 250A x .71 multiplier @100% =177.5, plus 120A x .84 m @100% = 100.8 plus, 120A x .84 @ 85%= 85.68 plus, 90A x .89m @70%= 56.01 total sum equals 420.05. Non conforming size allows next size up, per table 240.6 equals breaker size of 450A
I have said/thought that many times over the last 15 years.I love this community of threads so helpful.