I was reading an old thread about electric baseboard heat. How much on a circuit, continuous load, etc. It was if two 8' strips could be on a 20 amp circuit. At a continuous load that was 20.84 amps so the answer was no.
One poster suggested the voltage was probably over 240v so it might be ok. He was corrected by another poster who said in a strictly resistive load if the voltage goes up the current will go up in proportion.
I am trying to understand that. Wouldn't a1500 watt 6' baseboard heater at 240 volts would draw 6.25 amps, but if wired 120 volts draw 12.5 amps?
One poster suggested the voltage was probably over 240v so it might be ok. He was corrected by another poster who said in a strictly resistive load if the voltage goes up the current will go up in proportion.
I am trying to understand that. Wouldn't a1500 watt 6' baseboard heater at 240 volts would draw 6.25 amps, but if wired 120 volts draw 12.5 amps?