I am trying to determine that ampacitu needed for a restaurant. My question is when calculating ampacity for electric ranges (Mongolian table mounted grills),
Do I derate ampacity for the number of cooktops (30) @ 65% before applying 255.88? Each range has (5) 650 kw burners for 3250 kw each and are 120 v. So 30 is 97500
Times .65=63375
So is 63375 kv the number I would use to apply to 255.88? For the cooktops only, obviously.
Other loads I think I have a grasp on other loads just wanted to see if I am applying rules correctly for the cooktops
Do I derate ampacity for the number of cooktops (30) @ 65% before applying 255.88? Each range has (5) 650 kw burners for 3250 kw each and are 120 v. So 30 is 97500
Times .65=63375
So is 63375 kv the number I would use to apply to 255.88? For the cooktops only, obviously.
Other loads I think I have a grasp on other loads just wanted to see if I am applying rules correctly for the cooktops