When can a restraunt be wired in Romex?
You are just too slow.When it is built of Type III, IV or V construction and the construction is nonrated. Take a look at 334.10(3).
Also be aware that from a NEC standpoint NM cable is not permitted to be installed above a suspended or dropped ceiling. (See 334.12(A)(2))
Chris
The only thing I mentioned that you didn't was the rated construction part. NM cable is not permitted to be installed in a restaurant if the restaurant is built out of fire-rated construction.
Chris
Or if it meets the criteria of a place of assembly. Those rooms also would not be allowed to have nm cable.
Not exactly correct...NM can't be used if the building codes require the restaurant to be of fire rated construction. If the code would permit the building to be built of non-fire rated construction and it was built of fire rated construction, you could still use NM.The only thing I mentioned that you didn't was the rated construction part. NM cable is not permitted to be installed in a restaurant if the restaurant is built out of fire-rated construction.
Chris
Not exactly correct...NM can't be used if the building codes require the restaurant to be of fire rated construction. If the code would permit the building to be built of non-fire rated construction and it was built of fire rated construction, you could still use NM.
Not in my town.... Local codes...When can a restraunt be wired in Romex?