I'm doing some repairs on a retail store because "they had a little fire" and the fire department wrote up a list of electrical repairs and gave the owner 30 days to comply. The items are reasonable and not even a big deal, mostly.
Of course, the owner didn't even ask for a proposal unit two or three days before the compliance date. So, it's not done in time.
The fire guys are ok with that, but they want "ME" to make sure the owner has no code violations whether on their list or not. Not a really big deal but last I checked I don't get paid by San Mateo.
__________________________________________The Questions__________________________________________
90% of this is easy but there are some things I'm not sure of:
[1] There's a neon transformer with both low and high voltage terminals exposed. Shouldn't those be covered?
[2] They want all multioutlet Assy's secured. Is that code? If so, can they be secured to the floor?
[3] For equipment cords and multioutlet Assy' cords used for display and demo equipment, should those cords not be secured? Are they all treated the same?
[4] Aren't extension cords allowed for displays? And if so, can they be secured?
Of course, the owner didn't even ask for a proposal unit two or three days before the compliance date. So, it's not done in time.
The fire guys are ok with that, but they want "ME" to make sure the owner has no code violations whether on their list or not. Not a really big deal but last I checked I don't get paid by San Mateo.
__________________________________________The Questions__________________________________________
90% of this is easy but there are some things I'm not sure of:
[1] There's a neon transformer with both low and high voltage terminals exposed. Shouldn't those be covered?
[2] They want all multioutlet Assy's secured. Is that code? If so, can they be secured to the floor?
[3] For equipment cords and multioutlet Assy' cords used for display and demo equipment, should those cords not be secured? Are they all treated the same?
[4] Aren't extension cords allowed for displays? And if so, can they be secured?