HighVoltage4800
Member
- Location
- Detroit
Hello, I am a distribution lineman with a few questions. I work on the Delta and the Wye system. I have a question on the return path for a Delta system.
In a Wye system the return path is through the system neutral which is tapped at the center of the Wye back at the generator.
In a 3 phase Wye primary, there is 4 wires, 3 primary phases and a neutral.
Now in a Delta Primary, there is 3 wires, only 3 primary phases. So where is the return path back to the source?
Does it use the other phase as they reverse polarity due to the AC? When one is positive on the sine wave, electrons are flowing out through that conductor,
then when the other phase dips down to negative the electrons return back on that phase?
If this is the case, the system neutral on the Wye 3 phase is just for protection? IE phase to ground fault?
Second question is I understand how a transformer works but on our 4800v Delta when we wire a transformer, you put 2 phases of 2760 (phase to ground) into
the primary side of the transformer. H1 gets 2760v and H2 gets 2760v. If the Primary Coil is physically connected between the H1 and H2 how is this not a phase to phase fault?
Or is it not physically connected but induced like the secondary side? Same thing when we wire the same transformer to Wye. We change the tap changer on the transformer,
1 phase of 7620v goes into the H1 and then we put a ground into the H2. The ground is tapped to the pole ground, which is tapped to the system neutral and a driven ground rod.
How could that not cause a phase to ground fault?
Thanks guys.
In a Wye system the return path is through the system neutral which is tapped at the center of the Wye back at the generator.
In a 3 phase Wye primary, there is 4 wires, 3 primary phases and a neutral.
Now in a Delta Primary, there is 3 wires, only 3 primary phases. So where is the return path back to the source?
Does it use the other phase as they reverse polarity due to the AC? When one is positive on the sine wave, electrons are flowing out through that conductor,
then when the other phase dips down to negative the electrons return back on that phase?
If this is the case, the system neutral on the Wye 3 phase is just for protection? IE phase to ground fault?
Second question is I understand how a transformer works but on our 4800v Delta when we wire a transformer, you put 2 phases of 2760 (phase to ground) into
the primary side of the transformer. H1 gets 2760v and H2 gets 2760v. If the Primary Coil is physically connected between the H1 and H2 how is this not a phase to phase fault?
Or is it not physically connected but induced like the secondary side? Same thing when we wire the same transformer to Wye. We change the tap changer on the transformer,
1 phase of 7620v goes into the H1 and then we put a ground into the H2. The ground is tapped to the pole ground, which is tapped to the system neutral and a driven ground rod.
How could that not cause a phase to ground fault?
Thanks guys.