nizak

Senior Member
I had a conversation with another local contractor regarding the use of 4/0 4/0 2/0 AL USE.(3 Conductor Cable) for 200A residential services. Seems that he has been installing this cable for some time even in dwellings where there are no 240V appliances except for central air. I told him that to my understanding it was a code violation and that the grounded conductor had to be the same size as the ungrounded ones. He said that as long as there was any 240V load it could be derated 30%. He claims that it has never once been questioned.The whole conversation started when he stopped by a new house I was roughing in and noticed I use CU THHN and asked why I was doing my services the "expensive" way. I have used AL cable in the past but it was always 4/0 4/0 4/0. Am I wrong on this one?
 
So, the way I read it we can derate the portion of the range load, not the entire dwelling unit load.

NEC 220.61(B) said:
Permitted Reductions. A service or feeder supplying
the following loads shall be permitted to have an additional
demand factor of 70 percent applied to the amount in
220.61(B)(1) or portion of the amount
in 220.61(B)(2) determined
by the basic calculation:
(1) A feeder or service supplying household electric ranges,
wall-mounted ovens, counter-mounted cooking units, and
electric dryers, where the maximum unbalanced load has
been determined in accordance with Table 220.55 for
ranges and Table 220.54 for dryers
(2)...
 
So, the way I read it we can derate the portion of the range load, not the entire dwelling unit load.

That section allows an additional reduction for a range or dryer. You can use the basic calculation in 220.61(A) for the neutral load then are permiited the additional demand in (B).
 
I think you need to do what you feel most comfortable with, and what you think fits with the reputation of your company.

Yes, Contracting is competitive, but the NEC is also minimum safety, not necessarily good engineering design.
 
The grounded conductor can not be any smaller than the required grounding electrode conductor for a service or no smaller than the required equipment grounding conductor for other than services.

How your AHJ wants you to prove the load on the grounded conductor could be a different story. Many will allow you to reduce a size or two without showing any calculations, others may not.
 