bcm
Member
- Location
- Atlanta, Georgia
- Occupation
- Engineer
Happy Thursday, my sparky friends!
I have been asked to reuse a spare bucket in a 600A, 480V, 3 ph MCC to feed a 200A, 120/240V, 1 ph panelboard. I've never seen an MCC used for anything but serving motors in the past, but I haven't found anything in the NEC that prohibits serving a panelboard. It feels like a gray area code-wise.
As far as the design, the MCC is 600A, 480V 3 ph fed by 2 sets of (3) 350 MCM & 1#2 ground. The bucket is a spare from a removed 15 HP AC motor. Can I replace the "guts" (HOA, transformer, etc.) from the bucket with a 100A, 480V fuse or CB? I would then put a step-down transformer downstream which would bring voltage to 120/240 for the loadcenter, and wouldn't it also provide the required neutral?
Thanks so much for your input!
I have been asked to reuse a spare bucket in a 600A, 480V, 3 ph MCC to feed a 200A, 120/240V, 1 ph panelboard. I've never seen an MCC used for anything but serving motors in the past, but I haven't found anything in the NEC that prohibits serving a panelboard. It feels like a gray area code-wise.
As far as the design, the MCC is 600A, 480V 3 ph fed by 2 sets of (3) 350 MCM & 1#2 ground. The bucket is a spare from a removed 15 HP AC motor. Can I replace the "guts" (HOA, transformer, etc.) from the bucket with a 100A, 480V fuse or CB? I would then put a step-down transformer downstream which would bring voltage to 120/240 for the loadcenter, and wouldn't it also provide the required neutral?