greenspark1
Senior Member
- Location
- New England
The scenario is a facility with an older SquareD Model 5 motor control center. It currently feeds a number of motors, including a couple of ~5hp fans we are replacing. We are providing new fans and VFDs for them. I would like to reuse the feeds from the MCC and keep just the breaker in use in each bucket (remove overloads, contactors, etc). Then the breaker will feed a VFD (remote mounted), motor disconnect, then motor. Any issues reusing MCC buckets like this? The breakers will be instantaneous trip, but I think the VFD will provide all the remaining protection- mainly overload.
2nd, the fans out outside the building so I'd like to put VFDs inside, about 50' away. Any issues running VFD wiring this far? I'm reading some concerns about voltage reflections but haven't ever seen them before for VFDs. I'll put motor disconnects at each fan with early break contacts to tell the VFD to turn off.
2nd, the fans out outside the building so I'd like to put VFDs inside, about 50' away. Any issues running VFD wiring this far? I'm reading some concerns about voltage reflections but haven't ever seen them before for VFDs. I'll put motor disconnects at each fan with early break contacts to tell the VFD to turn off.