The AIC requirement will be lower at the 600V level.
OK, confirms my long hand calcs, wasn't sure I did correctly.
My 3 phase delta experience is typically with 3 phase motors and with 3 phase step down Y grounded transformers. In these transformers unbalanced loads go to neutral. Motors typically are balanced close enough there's no issue. But with step up trans with ungrounded delta supplying multiple single phase loads doesn't system end up with circulating currents?
Another concern is insulation rating of secondary conductors, 600v.
If secondary is ungrounded a phase fault will increase voltage on other phases to 830 v exceeding insulation rating. Also seems that it would impact secondary voltages on down stream single phase transformers if one of their primary legs went to 830 v.
Another trick from the DIY'r was to dual feed a transformer. Normal power through trans primary as step down from 600 to 208/120v, but in emergency gen set operation, generator feeds 120/208v y into secondary to feed 600 v 3 phase to facility distribution boards.
Sent from my iPad using Tapatalk