Revise 110.3(B)
George Stolz
Windsor, CO NEC: 2023
Hospital Master Electrician
1.) NEC Section/Paragraph: 110.3(B)
2.) Proposal Recommends: [revised text]
3.) Proposal: (B) Installation and Use. When listed or labeled equipment is installed, it shall be installed and used in accordance with any instructions included in the listing or labeling.
4.) Substantiation: As this section is currently written, it seems to require that listed or labeled equipment is required to be used. This would add clarity that unlisted equipment can be used, if it is approved by the Authority Having Jurisdiction.
Re: Revise 110.3(B)
I just had a thought: How about this instead:
3.) Proposal: Revise existing text and add an exception:
Exception: Other methods shall be permitted as approved by the Authority Having Jurisdiction, or as required by other sections of this code.
The exception allows for other methods that could be seen as violating listings; such as the methods prescribed in 300.20(B), for example.
[ June 05, 2005, 12:36 PM: Message edited by: georgestolz ]
Re: Revise 110.3(B)
I am blessed in that I get along pretty well with my AHJ's, and when I screw up, I usually have obviously screwed up. Some of my coworkers have had some issues along these lines. I write in their stead. :D
I'll try to shore up the substantiation soon. ;)