1.) NEC Section/Paragraph: 300.15(C)
2.) Proposal Recommends: [new text]
3.) Proposal: Add exception to 300.15(C)
Exception: A fitting shall not be required for type LFNC used for protection into concealed spaces.
4.) Substantiation: It is highly difficult to abrade cable assemblies with type LFNC conduit. This would ease installations from outdoor boxes to interior spaces.
2.) Proposal Recommends: [new text]
3.) Proposal: Add exception to 300.15(C)
Exception: A fitting shall not be required for type LFNC used for protection into concealed spaces.
4.) Substantiation: It is highly difficult to abrade cable assemblies with type LFNC conduit. This would ease installations from outdoor boxes to interior spaces.