A school district client has asked us to evaluate the power capacity and distribution in their HS and MS. Both schools have 480/277V switchboards as their main service entrance/disconnect, but are still utilizing large (2000A) sub-fed 208/120V switchboards for all distribution throughout the buildings (to 208V branch panels throughout). I assume voltage drop could be a concern, along with no spare breakers in most panels.
I'm proposing to re-distribute power throughout the buildings at 480V (from the 480V main switchboards), step down to 208V in local elec closets, and then install new 208V branch panels to re-feed all loads in the vicinity of those closets. However, we have no as-built documentation of the existing panels/distribution, so we don't know the calculated or actual load on any panel/switchboard in the buildings except the metered 480V main switchboard.
I've solicited proposals from local EC's to do 30-day metering on select panels to determine actual load on panels, but the prices are too high for this project. So now all we know is the MCB size or mains size in each branch panel. How can we properly group these panels, and size distribution panels (on both sides of the 480/208V transformers) to feed the grouped 208V branch panels, if we don't have any actual load data and metering them is cost prohibitive? If we just add up the amperages/ratings of the breakers/mains ratings, the sizes of our transformers and distribution panels will be outrageous (and we know current is additive like load is)?
Any advice or rules of thumb??? Thank you in advance.
I'm proposing to re-distribute power throughout the buildings at 480V (from the 480V main switchboards), step down to 208V in local elec closets, and then install new 208V branch panels to re-feed all loads in the vicinity of those closets. However, we have no as-built documentation of the existing panels/distribution, so we don't know the calculated or actual load on any panel/switchboard in the buildings except the metered 480V main switchboard.
I've solicited proposals from local EC's to do 30-day metering on select panels to determine actual load on panels, but the prices are too high for this project. So now all we know is the MCB size or mains size in each branch panel. How can we properly group these panels, and size distribution panels (on both sides of the 480/208V transformers) to feed the grouped 208V branch panels, if we don't have any actual load data and metering them is cost prohibitive? If we just add up the amperages/ratings of the breakers/mains ratings, the sizes of our transformers and distribution panels will be outrageous (and we know current is additive like load is)?
Any advice or rules of thumb??? Thank you in advance.