After a quick search on web, it can be thru either a phase converter or a variable frequency drive.A three phase motor requires 3 phase supply.
There wasn't any need for a three-phase motor. It was just a design choice for simplicity, longevity and low maintenance. If the building is big enough to require a powered revolving door, it's reasonable to assume that three-phase power would be available, and using a three-phase motor means eliminating the starting winding, the start/run capacitor(s), and the centrifugal start/run switch.... why we do need to go for a 3ph motor instead of 1ph particularly where the load is just 0.2 kw?
If motor is only 200W, maybe even can be done with just a capacitor or two? Kind of depends how much starting torque may be needed.Correct. The motor requires 3 phase power.
At 200W an electronic VFD is a cheap way to create 3 phase power from a single phase supply.
Would that mean the used motor is an AC Synchronous motor ?230429-0759 EDT
m sleem:
Ideally a three phase motor from fixed in space coils produces a constant amplitude rotating magnetic vector.
If you put a constant amplitude ( a DC magnet ) in that rotating field, then that magnet will lock on to the rotating field and rotate in space in sync with the rotating field. That is called a synchronous motor.
Would that mean the used motor is an AC Synchronous motor ?
You're right, frequency converter is mentioned with few hints for speed control, but wiring diagram does not indicate the inverter in details.......
In fact, a possibility not considered is that this revolving door already has internal VFDs for speed control. Do you have any documentation?
Please have a look at the attachments similar to our revolving door.If the equipment has an internal VFD, then it may be capable internally of converting single phase to three phase for the motor. The correct VFD can do this easily.
Unfortunately the wrong VFD will simply not work, or will fry itself, if you supply single phase power.
This will all come down to the documentation or instructions from the manufacturer. What range of supply voltage, frequency, and phase count will the system accept.
The fact that there is a 3 phase motor internal to the system is irrelevant.
Jon
Please have a look at the attachments similar to our revolving door.
Similar in that many VFD connection diagrams look nearly identical to that diagram regardless what the driven load is, so this sort of confirms that he has a VFD driven revolving door and that it likely intended to have single phase input and three phase output.That is the wiring diagram for a VFD being used to run a 3 phase induction motor using a single phase supply. It doesn't say anything about voltage or frequency limits, and the 0.2-2.2kW phrase suggests it is a general document, not for a specific apparatus.
You say "similar to our revolving door". What is the difference? Do you have the wiring diagram for your exact revolving door?
-Jon