...I am not familiar with an electrical acronym "RFS"...
Thanks.Recommended Fuse Size
Maybe C.B./fuse?Thanks.
IMO, we would need to know the MCA to apply 440.12.
Odd nameplate to have MOCP ratings of 42/38. European possibly ?
what is your opinion for using HACR C.B. for branch circuit if manufacturer indicates only fuse size on his nameplate?*
Thanks.
IMO, we would need to know the MCA to apply 440.12.
Odd nameplate to have MOCP ratings of 42/38. European possibly ?
I would agree. If the nameplate only mentions "fuse" and fails to mention "breaker" or "over current protection (non-specific)" then to meet mfg. specs you would need to protect the equipment by a fuse. I see that about on about 5% of my inspections, normally refrigeration equipment.In my opinion that would be a violation.
As a side note, most, if not all molded case breakers are now HACR.
http://static.schneider-electric.us...n/Molded Case Circuit Breakers/0600DB0102.pdf
I have never seen "recommended fuse size" on a piece of equipment. Make up your mind.Forgot to mention in the post. The unit is rated at 208V, 3ph. MCA is 25amps, recommended fuse size (RFS) is 30Amps and MOCP is 42Amps.
Would it be ok if I go with a 30A fused disconnect switch with 30A fuse in it?
I have never seen "recommended fuse size" on a piece of equipment. Make up your mind.
MCA is what size wire I use. MOCP is what I tie it to.
That is so weird.Mitsubishi for one does it. They will give you a MCA, a Recommended fuse size(or fuse/breaker size), and a MOCP. Personally I would size it to the recommended size.
Mitsubishi for one does it.
That is so weird.
How does one decide to go above the RFS? Once someone decides to go over the RFS do they go straight to MOCP or just the next size up?