If a wire type equipment ground is included in the run and the RGS properly bonded at the termination points, bonding would be accomplished.

The exception to 514.8 is a good example
 
As Augie stated the RMC would be bonded on one end which takes care of the bonding requirement for a metallic raceway. The EGC will bond the equipment on the other end.
 