A Alwayslearningelec Senior Member Location NJ Occupation Estimator Sep 21, 2023 #1 I have a run of RGS that transitions to PVC underground. This run would not be bonded because of the PVC correct?
I have a run of RGS that transitions to PVC underground. This run would not be bonded because of the PVC correct?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 21, 2023 #2 If a wire type equipment ground is included in the run and the RGS properly bonded at the termination points, bonding would be accomplished. The exception to 514.8 is a good example
If a wire type equipment ground is included in the run and the RGS properly bonded at the termination points, bonding would be accomplished. The exception to 514.8 is a good example
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Sep 21, 2023 #3 As Augie stated the RMC would be bonded on one end which takes care of the bonding requirement for a metallic raceway. The EGC will bond the equipment on the other end.
As Augie stated the RMC would be bonded on one end which takes care of the bonding requirement for a metallic raceway. The EGC will bond the equipment on the other end.