RGS and PVC Run

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If a wire type equipment ground is included in the run and the RGS properly bonded at the termination points, bonding would be accomplished.

The exception to 514.8 is a good example
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As Augie stated the RMC would be bonded on one end which takes care of the bonding requirement for a metallic raceway. The EGC will bond the equipment on the other end.
 