If a wire EGC is pulled with CCC, for feeder to separte structure, can the RGS be utlized as a grounding electrode? If not code section forbiding please.
If a wire EGC is pulled with CCC, for feeder to separte structure, can the RGS be utlized as a grounding electrode? If not code section forbiding please.
On a very strange day, in a neighborhood far, far from here, you may be able to use a metal conduit as a GE. Only where you encounter rock bottom driving an 8ft. rod or pipe electrode at 45° would you permitted to use a conduit buried in a trench not less than 30in. deep. See 250.52(A)(5)(a) and 250.53(G).
I'd just like to hear about anyone making attempt to get it off the ground, regardless of the outcome. :happyyes:You are absolutely correct in what it says.
Good luck getting an inspector to accept that would apply to a conduit containing a feeder or branch circuit and before you point out the code does not say that, I know and I still maintain it wont fly.![]()
If a wire EGC is pulled with CCC, for feeder to separte structure, can the RGS be utlized as a grounding electrode? If not code section forbiding please.
I beg to differ...The code allows pipe type electrodes. It does not allow for conduit to be used as an electrode.
Having said that, it is a stupid distinction but that is what the code actually says. It also says the pipe type electrode would have to be driven in most cases.
(5) Rod and Pipe Electrodes. Rod and pipe electrodes
shall not be less than 2.44 m (8 ft) in length and shall
consist of the following materials.
(a) Grounding electrodes of pipe or conduit shall not
be smaller than metric designator 21 (trade size 3⁄4) and,
where of steel, shall have the outer surface galvanized or
otherwise metal-coated for corrosion protection.
(b) Rod-type grounding electrodes of stainless steel
and copper or zinc coated steel shall be at least 15.87 mm
(5⁄8 in.) in diameter, unless listed.
I agree it seems to be allowed to be used as an electrode under 250.52(A)(5). If not then it would at least fit under (A)(8).I beg to differ...
You won't get any argument from me as long as it is at least 3/4" conduit, at least 8ft. buried, and one point is at least 8ft. underground.... No one has convinced me such an install would not be code complient...
No one has convinced me such an install would not be code complient,